Default Avaya 3510GT-PWR+

I have 4 Avaya 3510GT-PWR+ switches, I have them all in fanless mode and a few of them are mounted to drywall. When the switches are in fanless mode they become really hot even though I am not using any PoE devices. I may sound a little crazy but is there any possibility that the switches could start a fire due to the heat. They are in areas with decent airflow but I am not a thermal engineer.

All comments would be beneficial, Thanks.
Reply With Quote
  #2  
Old 10-12-2014, 05:33 AM
jburba jburba is offline
Member
 
Join Date: Oct 2014
Posts: 6
jburba has 10 reputation points
Default

Same here. In EDM, I was monitoring the temperature and it was reaching 54C which is above its posted operating temperature range of 0-50C. I disabled POE and shutdown all ports that were not being used and those that were, 3 of them at the moment, I was using in 802.3af mode. I have it mounted on dry wall, with a good distance to any walls and the fan unobstructed, but it was getting hotter than I was comfortable with. The unit is mounted in a closet, without AC, but more than adequate ventilation. With the fan on, high-power mode, it drops it to 35C. I'm guessing they are meant to be run with the fan on, if not kept in a cooled network closet.

As some clarification, I work in IT, and I use the 8 port POE+ switch at home with some network security cams and some access points. My employer uses the 48 port ones in stacks so I am familiar with them, but the 48 port ones are always run fan on or in a cooled server room. I never bothered to see what the requirements for cooling was for the devices before hand. Unless the sound is distruptive, just run it in fan mode, it is not silent, but it is whisper quiet.

That said, can anyone chime in as to what settings are best to reduce energy use (ie less heat production)?
Reply With Quote
  #3  
Old 10-14-2014, 02:56 PM
zakabog zakabog is offline
Genius
 
Join Date: Aug 2014
Posts: 300
zakabog has 25 to 49 reputation pointszakabog has 25 to 49 reputation pointszakabog has 25 to 49 reputation points
Default

The switch will fail well before it gets hot enough to start a fire, the ignition temperature of paper is around 220C. The switches CPU running with no fans is what's causing the temperature to spike. Is there any reason you have it running in fanless mode in an environment that isn't temperature controlled?
Reply With Quote
  #4  
Old 10-23-2014, 05:58 AM
jburba jburba is offline
Member
 
Join Date: Oct 2014
Posts: 6
jburba has 10 reputation points
Default

I have been tinkering with mine. CPU pretty much does cpu things, so I disabled all remote access save ssh. I also made alterations, at my own risk, to the chassis, namely drilling holes and creating a pretty nice design on it. That said I ran it without the chassis cover for some bit. Most of the heat production is not even coming from the CPU, but the built-in power brick. This is why no matter how little devices you connect to POE, it starts hot, as just being on, produces heat for the brick. This is why without the chassis cover, it ran at most at 43C with 4 POE devices connected and no fan on. With the chassis on, it keeps the heat in and the fan is positioned right where the brick is, so it is meant to pull hot air from there not the cpu, because again the CPU is fine. With the fan off, the heat from the brick, the boxed in chassis makes it a convection oven. I'm drilling more holes into my cover for both air circulation and added surface area. Since it is aluminum, it will help dissipate heat better if I sand off the paint and expose the aluminum. Again this is just me, taking my own risks, with my own devices, but you can use what I learned as you wish. From this, my conclusion is that this device is not meant to run fanless, thought the option is nice, in room temperature closet, or area. In a temperature controlled server room, like at my job, it'll be fine, but from the small size of the fan, the savings will be just pittance.
Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -7. The time now is 05:51 PM.

This Forum is provided solely for the use and convenience of Avaya customers and partners. Use of the Forum is subject to the Terms and Use and Privacy Statement found at www.avaya.com. No other use is permitted. The Forum including all content posted is “AS IS” and Avaya expressly disclaims all warranties and/or guarantees as to its accuracy, reliability, usefulness, quality or non-infringement of intellectual property. Avaya reserves the right to remove any content posted on the Forum at any time and for whatever reason.

Avaya will not be liable for any content posted on this Forum, including, without limitation, any errors or omissions or for any losses or damages of any kind incurred as a result of use or reliance on any content, regardless of its origin.

You expressly understand and agree that you assume all risks associated with use or reliance on this content.